Based on observation and interview, the facility failed to ensure the required Type 1 essential electrical system (EES) and generator was in place and operational prior to accepting a ventilator assisted resident where an emergency electrical power system would be needed to maintain life support equipment in the event of a power outage for 1 of 1 sampled residents (10) reviewed for respiratory services. This was determined to be an Immediate Jeopardy to not have the necessary Type 1 EES system and placed residents at risk of death if an emergency occurred. This failure placed residents at risk in case of a power outage and needing respiratory support. …
F906 citations in Washington
Environmental Deficiencies
Provide enough power supply for lighting all entrances and exits; equipment for fire detection and alarm systems, and extinguishers.
Data as of , released by CMS on October 8, 2026. Source: CMS Provider Data Catalog.
Against expectation — 2023
Washington cites F906 more often than its own record predicts
43.80 times the share F906 takes of citations nationally.
Of every deficiency written in Washington in 2023, this is the portion that was F906.
Each state is measured against its own expected share, not against other states.
In the surveyor’s words
What Washington surveyors wrote
F906 findings written in Washington, one from each severity band recorded here, most serious first.
Severity is as the surveyor wrote it. Some findings had already been corrected before the survey.