Deficiency Index

F906 citations in Illinois

Environmental Deficiencies

Provide enough power supply for lighting all entrances and exits; equipment for fire detection and alarm systems, and extinguishers.

Data as of , released by CMS on October 8, 2026. Source: CMS Provider Data Catalog.

F906 in Illinois. Pick another state for the same tag.

No F906 citations were recorded in Illinois for 2025. That means none appear in the CMS file for that year — not that the requirement does not apply.

In the surveyor’s words

What Illinois surveyors wrote

F906 findings written in Illinois, one from each severity band recorded here, most serious first.

Severity is as the surveyor wrote it. Some findings had already been corrected before the survey.

L · Immediate jeopardy, widespreadFebruary 25, 2026

Based on interview and record review, the facility experienced a power failure related to an area wide power outage. The facility's backup generator failed to provide back up power for the facility as it is designed to do during a power outage. The facility failed to ensure the safety of all residents dependent on life-sustaining equipment related to inability to provide electricity to life sustaining devices during the power failure. The facility failed to document the generator was in working order by completed weekly testing and monthly testing under load to ensure the backup generators availability in an emergency. …